A direct-acting proportional controller is being used with a direct-acting transmitter to control the temperature of lube oil exiting a heat exchanger ___

A direct-acting proportional controller is being used with a direct-acting transmitter to control the temperature of lube oil exiting a heat exchanger.

The controllers proportional band is 70°F to 120°F.

Which one of the following will be the controller’s output percentage when the measured lube oil temperature is 83°F?

A. 13 percent
B. 26 percent
C. 37 percent
D. 74 percent

Show Answer

Answer: B