The following steps are to be taken while calibrating:
-
Adjust zero of the Transmitter
-
Static pressure test : Give equal pressure on both sides of the transmitter. Zero should not shift. If it is shifting carry out static alignment.
-
Vacuum test : Apply equal vacuum to both the sides. The zero should not shift.
-
Calibration Procedure: . Give 20 psi air or 24Vdc supply to the transmitter. . Vent the L.P. side to atmosphere. . Connect output of the Instrument to a standard test gauge or Multimeter and adjust zero.
-
Apply required pressure to high pressure side of the transmitter and adjust the span.
-
Adjust zero again if necessary.