100 Top Power System Protection Questions and Answers
Q:What are the functions of protective relays
To detect the fault and initiate the operation of the circuit breaker to isolate
the defective element from the rest of the system, thereby protecting the system from damages consequent to the fault.
Q: Give the consequences of short circuit.
Whenever a short-circuit occurs, the current flowing through the coil increases to an enormous value. If protective relays are present, a heavy current also flows through the relay coil, causing it to operate by closing its contacts.
The trip circuit is then closed , the circuit breaker opens and the fault is isolated from the rest of the system. Also, a low voltage may be created which may damage systems connected to the supply.
Q: Define protected zone.
Are those which are directly protected by a protective system such as relays,
fuses or switchgears. If a fault occurring in a zone can be immediately detected and or isolated by a protection scheme dedicated to that particular zone.
Q: What are unit system and non unit system?
A unit protective system is one in which only faults occurring within its
protected zone are isolated. Faults occurring elsewhere in the system have no influence on the operation of a unit system. A non unit system is a protective system which is activated even when the faults are external to its protected zone.
Q: What is primary protection?
Is the protection in which the fault occurring in a line will be cleared by its
own relay and circuit breaker. It serves as the first line of defence.
Q: What is back up protection?
Is the second line of defence , which operates if the primary protection
fails to activate within a definite time delay.
Q: Name the different kinds of over current relays.
Induction type non-directional over current relay, Induction type directional
over current relay & current differential relay.
Q: Define energizing quantity.
It refers to the current or voltage which is used to activate the relay into
operation.
Q: Define operating time of a relay.
It is defined as the time period extending from the occurrence of the
fault through the relay detecting the fault to the operation of the relay.
Q: Define resetting time of a relay.
It is defined as the time taken by the relay from the instant of isolating
the fault to the moment when the fault is removed and the relay can be reset.
Q: What are over and under current relays?
Overcurrent relays are those that operate when the current in a line exceeds a
predetermined value. (eg: Induction type non-directional/directional overcurrent relay, differential overcurrent relay)whereas undercurrent relays are those which operate whenever the current in a circuit/line drops below a predetermined value.(eg: differential over-voltage relay)
Q: Mention any two applications of differential relay.
Protection of generator & generator transformer unit; protection of large motors
and busbars .
Q:What is biased differential bus zone reduction?
The biased beam relay is designed to respond to the differential current in terms
of its fractional relation to the current flowing through the protected zone. It is essentially an over-current balanced beam relay type with an additional restraining coil. The restraining coil produces a bias force in the opposite direction to the operating force.
Q: What is the need of relay coordination?
The operation of a relay should be fast and selective, ie, it should isolate the fault in the shortest possible time causing minimum disturbance to the system.
Also, if a relay fails to operate, there should be sufficiently quick backup protection so that the rest of the system is protected. By coordinating relays, faults can always be isolated quickly without serious disturbance to the rest of the system.
Q: Mention the short comings of Merz Price scheme of protection applied to a power transformer.
In a power transformer, currents in the primary and secondary are to be compared. As these two currents are usually different, the use of identical transformers will give differential current, and operate the relay under no-load condition.
Also, there is usually a phase difference between the primary and secondary currents of three phase transformers. Even CT’s of proper turn-ratio are used, the differential current may flow through the relay under normal condition.
Q:What are the various faults to which a turbo alternator is likely to be subjected?
Failure of steam supply; failure of speed; overcurrent; over voltage; unbalanced
loading; stator winding fault .
Q: What is an under frequency relay?
An under frequency relay is one which operates when the frequency of the system (usually an alternator or transformer) falls below a certain value.
Q: Define the term pilot with reference to power line protection.
Pilot wires refers to the wires that connect the CT’s placed at the ends of a power transmission line as part of its protection scheme. The resistance of the pilot wires is usually less than 500 ohms.
Q: Mention any two disadvantage of carrier current scheme for transmission line only.
The program time (ie, the time taken by the carrier to reach the other end-upto
.1% mile); the response time of band pass filter; capacitance phase-shift of the
transmission line .
Q: What are the features of directional relay?
High speed operation; high sensitivity; ability to operate at low voltages; adequate short-time thermal ratio; burden must not be excessive.
Q: What are the causes of over speed and how alternators are protected from it?
Sudden loss of all or major part of the load causes over-speeding in alternators.
Modern alternators are provided with mechanical centrifugal devices mounted on their driving shafts to trip the main valve of the prime mover when a dangerous over-speed occurs.
Q: What are the main types of stator winding faults?
Fault between phase and ground; fault between phases and inter-turn fault
involving turns of the same phase winding.
Q: Give the limitations of Merz Price protection.
Since neutral earthing resistances are often used to protect circuit from earth-fault currents, it becomes impossible to protect the whole of a star-connected alternator. If an earth-fault occurs near the neutral point, the voltage may be insufficient to operate the relay.
Also it is extremely difficult to find two identical CT’s. In addition to this, there always an inherent phase difference between the primary and the secondary quantities and a possibility of current through the relay even when there is no fault.
Q:What are the uses of Buchholz’s relay?
Bucholz relay is used to give an alarm in case of incipient( slow-developing)
faults in the transformer and to connect the transformer from the supply in the event of severe internal faults. It is usually used in oil immersion transformers with a rating over 750KVA.
Q: What are the types of graded used in line of radial relay feeder?
Definite time relay and inverse-definite time relay.
Q: What are the various faults that would affect an alternator?
(a) Stator faults
1, Phase to phase faults
2, Phase to earth faults
3, Inter turn faults
(b)
1, Earth faults
2, Fault between turns
3, Loss of excitation due to fuel failure
c) 1, Over speed
2, Loss of drive
3, Vacuum failure resulting in condenser pressure rise, resulting in
shattering of the turbine low pressure casing
(d) 1, Fault on lines
2, Fault on busbars
Q: Why neutral resistor is added between neutral and earth of an alternator?
In order to limit the flow of current through neutral and earth a resistor is
introduced between them.
Q: What is the backup protection available for an alternator?
Overcurrent and earth fault protection is the backup protections.
Q: What are faults associated with an alternator?
(a) External fault or through fault
(b) Internal fault
1, Short circuit in transformer winding and connection
2, Incipient or slow developing faults
Q:What are the main safety devices available with transformer?
Oil level guage, sudden pressure delay, oil temperature indicator, winding
temperature indicator .
Q: What are the limitations of Buchholz relay?
(a) Only fault below the oil level are detected.
(b) Mercury switch setting should be very accurate, otherwise even for
vibration, there can be a false operation.
© The relay is of slow operating type, which is unsatisfactory.
Q: What are the problems arising in differential protection in power transformer and how are they overcome?
- Difference in lengths of pilot wires on either sides of the relay. This is
overcome by connecting adjustable resistors to pilot wires to get equipotential
points on the pilot wires. - Difference in CT ratio error difference at high values of short circuit currents
that makes the relay to operate even for external or through faults. This is
overcome by introducing bias coil. - Tap changing alters the ratio of voltage and currents between HV and LV sides
and the relay will sense this and act. Bias coil will solve this. - Magnetizing inrush current appears wherever a transformer is energized on its
primary side producing harmonics. No current will be seen by the secondary.
CT’s as there is no load in the circuit. This difference in current will actuate the
differential relay. A harmonic restraining unit is added to the relay which will
block it when the transformer is energized.
Q:What is REF relay?
It is restricted earth fault relay. When the fault occurs very near to the neutral
point of the transformer, the voltage available to drive the earth circuit is very small, which may not be sufficient to activate the relay, unless the relay is set for a very low current. Hence the zone of protection in the winding of the transformer is restricted to cover only around 85%. Hence the relay is called REF relay.
Q:What is over fluxing protection in transformer?
If the turns ratio of the transformer is more than 1:1, there will be higher core loss and the capability of the transformer to withstand this is limited to a few minutes only. This phenomenon is called over fluxing.
Q: Why busbar protection is needed?
(a) Fault level at busbar is high
(b) The stability of the system is affected by the faults in the bus zone.
© A fault in the bus bar causes interruption of supply to a large portion of the
system network.
Q: What are the merits of carrier current protection?
Fast operation, auto re-closing possible, easy discrimination of simultaneous
faults .
Q: What are the errors in CT?
(a) Ratio error
Percentage ratio error = [(Nominal ratio – Actual ratio)/Actual ratio] x 100
The value of transformation ratio is not equal to the turns ratio.
(b) Phase angle error:
Phase angle =180/ [(ImCos -I1Sin )/nIs]
Q: What is field suppression?
When a fault occurs in an alternator winding even though the generator circuit
breaker is tripped, the fault continues to fed because EMF is induced in the generator itself. Hence the field circuit breaker is opened and stored energy in the field winding is discharged through another resistor. This method is known as field suppression.
Q: What are the causes of bus zone faults?
Failure of support insulator resulting in earth fault
Flashover across support insulator during over voltage
Heavily polluted insulator causing flashover
Earthquake, mechanical damage etc.
Q: What are the problems in bus zone differential protection?
Large number of circuits, different current levels for different circuits for
external faults.
Saturation of CT cores due to dc component and ac component in short
circuit currents. The saturation introduces ratio error.
Sectionalizing of the bus makes circuit complicated.
Setting of relays need a change with large load changes.
Q: What is static relay?
It is a relay in which measurement or comparison of electrical quantities is made in a static network which is designed to give an output signal when a threshold condition is passed which operates a tripping device.
Q: What is power swing?
During switching of lines or wrong synchronization surges of real and reactive
power flowing in transmission line causes severe oscillations in the voltage and current vectors. It is represented by curves originating in load regions and traveling towards relay characteristics.
Q: What is a programmable relay?
A static relay may have one or more programmable units such as microprocessors or microcomputers in its circuit.
Q: What is CPMC?
It is combined protection, monitoring and control system incorporated in the static system.
Q:What are the advantages of static relay over electromagnetic relay?
o Low power consumption as low as 1mW
o No moving contacts; hence associated problems of arcing, contact bounce,
erosion, replacement of contacts
o No gravity effect on operation of static relays. Hence can be used in
vessels ie, ships, aircrafts etc.
o A single relay can perform several functions like over current, under
voltage, single phasing protection by incorporating respective functional
blocks. This is not possible in electromagnetic relays
o Static relay is compact
o Superior operating characteristics and accuracy
o Static relay can think , programmable operation is possible with static
relay
o Effect of vibration is nil, hence can be used in earthquake-prone areas
o Simplified testing and servicing. Can convert even non-electrical
quantities to electrical in conjunction with transducers.
Q: What is resistance switching ?
It is the method of connecting a resistance in parallel with the contact space(arc).
The resistance reduces the restriking voltage frequency and it diverts part of the arc current. It assists the circuit breaker in interrupting the magnetizing current and capacity current.
Q:What do you mean by current chopping?
When interrupting low inductive currents such as magnetizing currents of the
transformer, shunt reactor, the rapid deionization of the contact space and blast effect may cause the current to be interrupted before the natural current zero. This phenomenon of interruption of the current before its natural zero is called current chopping.
Q: What are the methods of capacitive switching?
• Opening of single capacitor bank
• Closing of one capacitor bank against another
Q: What is an arc?
Arc is a phenomenon occurring when the two contacts of a circuit breaker
separate under heavy load or fault or short circuit condition.
Q: Give the two methods of arc interruption?
High resistance interruption:-the arc resistance is increased by elongating, and
splitting the arc so that the arc is fully extinguished
Current zero method:-The arc is interrupted at current zero position that
occurs100 times a second in case of 50Hz power system frequency in ac.
Q: What is restriking voltage?
It is the transient voltage appearing across the breaker contacts at the instant of arc being extinguished.
Q:What is meant by recovery voltage?
The power frequency rms voltage appearing across the breaker contacts after the arc is extinguished and transient oscillations die out is called recovery voltage.
Q:What is RRRV?
It is the rate of rise of restriking voltage, expressed in volts per microsecond. It is closely associated with natural frequency of oscillation.
Q: What is circuit breaker?
It is a piece of equipment used to break a circuit automatically under fault
conditions. It breaks a circuit either manually or by remote control under normal
conditions and under fault conditions.
Q: Write the classification of circuit breakers based on the medium used for arc extinction?
- Air break circuit breaker
- Oil circuit breaker
- Minimum oil circuit breaker
- Air blast circuit breaker
- SF6 circuit breaker
- Vacuum circuit breaker
Q: What is the main problem of the circuit breaker?
When the contacts of the breaker are separated, an arc is struck between them.
This arc delays the current interruption process and also generates enormous heat which may cause damage to the system or to the breaker itself. This is the main problem.
Q: What are demerits of MOCB?
- Short contact life
- Frequent maintenance
- Possibility of explosion
- Larger arcing time for small currents
- Prone to restricts
Q: What are the advantages of oil as arc quenching medium?
• It absorbs the arc energy to decompose the oil into gases, which have
excellent cooling properties
• It acts as an insulator and permits smaller clearance between line conductors
and earthed components
Q:What are the hazards imposed by oil when it is used as an arc quenching medium?
There is a risk of fire since it is inflammable. It may form an explosive mixture
with arc. So oil is preferred as an arc quenching medium.
Q: What are the advantages of MOCB over a bulk oil circuit breaker?
• It requires lesser quantity of oil
• It requires smaller space
• There is a reduced risk of fire
• Maintenance problem are reduced
Q: What are the disadvantages of MOCB over a bulk oil circuit breaker?
o The degree of carbonization is increased due to smaller quantity of oil
o There is difficulty of removing the gases from the contact space in time
o The dielectric strength of the oil deteriorates rapidly due to high degree of
carbonization.
Q: What are the types of air blast circuit breaker?
- Arial-blast type
- Cross blast
- Radial-blast
Q: What are the advantages of air blast circuit breaker over oil circuit breaker?
o The risk of fire is diminished
o The arcing time is very small due to rapid buildup of dielectric strength
between contacts
o The arcing products are completely removed by the blast whereas oil
deteriorates with successive operations
Q:What are the demerits of using oil as an arc quenching medium?
• The air has relatively inferior arc quenching properties
• The air blast circuit breakers are very sensitive to variations in the rate of rise
of restriking voltage
• Maintenance is required for the compression plant which supplies the air blast
Q: What is meant by electro negativity of SF6 gas?
SF6 has high affinity for electrons. When a free electron comes and collides with
a neutral gas molecule, the electron is absorbed by the neutral gas molecule and negative ion is formed. This is called as electro negativity of SF6 gas.
Q: What are the characteristic of SF6 gas?
It has good dielectric strength and excellent arc quenching property. It is inert,
non-toxic, noninflammable and heavy. At atmospheric pressure, its dielectric strength is 2.5 times that of air. At three times atmospheric pressure, its dielectric strength is equal to that of the transformer oil.
Q: Write the classifications of test conducted on circuit breakers.
- Type test
- Routine test
- Reliability test
- Commissioning test
Q: What are the indirect methods of circuit breaker testing?
o Unit test
o Synthetic test
o Substitution testing
o Compensation testing
o Capacitance testing
Q: What are the advantages of synthetic testing methods?
• The breaker can be tested for desired transient recovery voltage and RRRV.
• Both test current and test voltage can be independently varied. This gives
flexibility to the test
• The method is simple
• With this method a breaker capacity (MVA) of five time of that of the
capacity of the test plant can be tested.
Q: How does the over voltage surge affect the power system?
The over voltage of the power system leads to insulation breakdown of the
equipments. It causes the line insulation to flash over and may also damage the nearby transformer, generators and the other equipment connected to the line.
Q: What is pick up value?
It is the minimum current in the relay coil at which the relay starts to
operate.
Q:. Define target.
It is the indicator used for showing the operation of the relay.
Q: Define reach.
It is the distance upto which the relay will cover for protection.
Q: Define blocking .
It means preventing the relay from tripping due to its own characteristics or due to additional relays.
Q: Mention any 2 applications of differential relays.
Protection of generator and generator-transformer unit: protection of
large motors and bus bars
Q:Mention the various tests carried out in a circuit breaker at HV labs.
Short circuit tests, Synthetic tests& direct tests.
Q: Mention the advantages of field tests.
The circuit breaker is tested under actual conditions like those that occur in the
network.
Special occasions like breaking of charging currents of long lines ,very short line
faults ,interruption of small inductive currents etc… can be tested by direct testing only.
Q: State the disadvantages of field tests.
The circuit breaker can be tested at only a given rated voltage and network
capacity.
The necessity to interrupt the normal services and to test only at light load
conditions.
Extra inconvenience and expenses in installation of controlling and
measuring equipment in the field.
Q : Define composite testing of a circuit breaker.
In this method the breaker is first tested for its rated breaking capacity at a
reduced voltage and afterwards for rated voltage at a low current.This method does not give a proper estimate of the breaker performance.
Q: State the various types of earthing.
Solid earthing, resistance earthing , reactance earthing , voltage transformer
earthing and zig-zag transformer earthing.
Q: What are arcing grounds?
The presence of inductive and capacitive currents in the isolated neutral system
leads to formation of arcs called as arcing grounds.
Q: What is arc suppression coil?
A method of reactance grounding used to suppress the arc due to arcing
grounds.
Q:State the significance of single line to ground fault.
In single line to ground fault all the sequence networks are connected
in series. All the sequence currents are equal and the fault current magnitude is three times its sequence currents.
Q: What are symmetrical components?
It is a mathematical tool to resolve unbalanced components into balanced
components.
Q: State the three sequence components.
Positive sequence components, negative sequence components and zero
sequence components.
Q: Define positive sequence component.
-has 3 vectors equal in magnitude and displaced from each other by an angle
120 degrees and having the phase sequence as original vectors.
Q: Define zero sequence component.
They has 3 vectors having equal magnitudes and displaced from each
other by an angle zero degrees.
Q: State the significance of double line fault.
It has no zero sequence component and the positive and negative sequence
networks are connected in parallel.
Q: Define negative sequence component.
It has 3 vectors equal in magnitude and displaced from each other by an angle
120 degrees and has the phase sequence in opposite to its original phasors.
Q: State the different types of faults.
Symmetrical faults and unsymmetrical faults and open conductor faults.
Q: State the various types of unsymmetrical faults.
Line to ground ,line to line and double line to ground faults
Q: Mention the withstanding current in our human body.
9mA
Q: State the different types of circuit breakers.
Air ,oil,vacuum circuit breakers.
Q: Define per unit value.
It is defined as the ratio of actual value to its base value.
Q:. Mention the inductance value of the peterson’s coil.
L=1/3wc2
Q: Define single line diagram.
Representation of various power system components in a single line is
defined as single line diagram.
Q: Differentiate between a fuse and a circuit breaker.
Fuse is a low current interrupting device. It is a copper or an aluminium wire. Circuit breaker is a high current interrupting device and it act as a switch
under normal operating conditions.
Q: How direct tests are conducted in circuit breakers?
Using a short circuit generator as the source.
Using the power utility system or network as the source.
Q: What is dielectric test of a circuit breaker?
It consists of overvoltage withstand test of power frequency lightning and impulse voltages.Testa are done for both internal and external insulation
with switch in both open and closed conditions.