32767 value when i connect my transmitter to the AI of S7-400 PLC

I’m getting the 32767 value as the max value when i connect my 4-20 mA transmitter to the AI of S7-400. But the issue now is the value 32767 remains even when i disconnect the transmitter. Is that normal?

Answer:

Yes. It’s normal. It’s call wire break. CPU can’t process the input.

Author: Ashu