Can we do stroke test with 4-20mA source?

Is it possible to stroke test the valve with the 4-20mA source while we have foundation fieldbus type positioner?

stroke test the valve with the 4-20mA source

Positioner make is METSO, ND9103-FX.

It is not possible to do the stroke test using a 4 to 20 mA source meter for Foundation-Fieldbus (FF) based instruments.

You can connect the HART communicator (FF type) to the valve positioner and carry out the control valve stroke test.

You can also use the valve positioner display for stroke test (some vendors provide this option).