Hi, my DP transmitter Rosemount 3051 Coplanar type and impulse lines high and low connected wrong. due to wrong connection display indicate minus value. How can i change direction from field communicator menu trees. i cannot find this place.
Apply different ranges which includes negative and positive values then check.
Note: Your instrument/sensor will fail soon with wrong connections. Measurement is not possible with wrong range, its only to get some +ve value on the instrument display.
I think you know what you are doing otherwise correct the installation.
While I don’t think it is the greatest of ideas and considering that it is a flow it may not be possible.
However, if you change your range from say 0-100 " H2O to -100 -0 " H2O you should be able to achieve the same mA out put to your control system therefore getting a correct reading. Essentially no different than using a wet leg on you LP side of a level.
Also I do not see why you would damage your diaphragm seeing how both sensors would be sitting in the same line pressure essentially. Then again I am not certain this would work just spit balling an idea.
The easiest fix would just be to fix the mistake and swap your impulse lines rather than doing a bunch of paper work and working on my theory.
So while my little theory sounds and reads good. I do not think it would work lol. You may not be able to compensate the pressure drop across the orifice with the impulse lines reversed.