The procedure for glycol filling is:
- Close the primary isolation valves.
- Open the vent on the seal pots.
- Drain the used glycol if present.
- Connect a hand pump on L.P. side while filling the H.P. side with glycol.
- Keep the equalizer valve open.
- Keep the L.P. side valve closed.
- Start pumping and fill glycol. .
- Same repeat for L.P. side by connecting pump to H.P. side, keeping equalizer open and H.P isolation valve closed.
- Close the seal pot vent valves.
- Close equalizer valve.
- Open both the primary isolation valves.