ON/OFF Valves Loop Checks Procedure
-
Valve response time shall be recorded in loop record sheet.
-
Check and verify the DCS / ESD configuration for applicable points.
-
If any ESD logic / interlocking are involved in applicable loop to energized solenoid valve, should be prepared ESD points on functional logic and same procedure to be carried out for DCS logic.
-
If instrument air supply is not available then connect nitrogen cylinder. In big size of valve cases, big volume of nitrogen will be required then in that case on/off valves function test will be executed upon air supply availability.
-
Apply the command from DCS / field for open and close as applicable.
-
Verifying the corresponding valves position in DCS and field.
-
Verify the partial stroke function test of âZVâ.
-
Verify the valve action on air supply failure.
-
Check the hand wheel / hand jack manual operation / function as applicable.
-
Normally On/Off valve loop test should be performed after completion of the external air supply piping works. In some cases when required, loop test can be executed without air.
-
In case of air piping is not installed and tested then this exception item to be mentioned in the loop test exception log sheet prior to signing the loop folder.
-
Loop will be initiated only and signed after the clearance of the punch list.