Refer to the drawing of a simple chromel-alumel thermocouple circuit. The thermocouple, thermocouple connection head, and reference junction panel are located inside a reactor building (RB) while the temperature instrument is located outside the RB ___

Refer to the drawing of a simple chromel-alumel thermocouple circuit (see figure below).

The thermocouple, thermocouple connection head, and reference junction panel are located inside a reactor building (RB) while the temperature instrument is located outside the RB.

Thermocouple temperature indication is initially 440°F.

A steam leak inside the RB increases the temperatures of the thermocouple connection head and reference junction panel by 40°F, while the temperature at the measuring tip is unchanged.

What is the resulting temperature indication?

A. 400°F
B. 440°F
C. 480°F
D. 520°F

Show Answer

Answer: A

Share your understanding of this question with the correct explanation.