Standard Inverse Overcurrent Relay connected to the current transformer (CT) with ___

Standard Inverse Overcurrent Relay connected to the current transformer (CT) with Current Ratio of 1000/5 A, TMS = 0.2, set at 100% if the current size is caused 5,000 A, relay operating time is

A. 0.43 seconds
B. 4.30 seconds
C. 0.80 seconds
D. 0.86 seconds

Show Answer

Answer: D