The tank is protected by a relief valve and a safety valve that both discharge to the atmosphere. The valves have the following characteristics ___

A completely full water storage tank is being hydrostatically tested to 200 psig using a positive displacement pump (PDP) with a smooth and constant discharge flow rate of 8 gpm.

The tank is protected by a relief valve and a safety valve that both discharge to the atmosphere.

The valves have the following characteristics:

  1. The relief valve opening setpoint is 220 psig with an accumulation of 5 percent.
  2. The safety valve opening setpoint is 260 psig with a blowdown of 5 percent.
  3. Both valves have a maximum discharge flow rate of 6 gpm.

The PDP is inadvertently left running when tank pressure reaches 200 psig.

After a few minutes with the PDP still running, the relief valve will be discharging a flow rate of approximately __________; and the safety valve will be __________.

A. 2 gpm; partially open
B. 6 gpm; partially open
C. 2 gpm; cycling between fully open and fully closed
D. 6 gpm; cycling between fully open and fully closed

Show Answer

Answer: D