Two generators rated 200 MW and 400 MW having governor droop characteristics ___

Two generators rated 200 MW and 400 MW having governor droop characteristics of 4% and 5% respectively are operating in parallel.

If the generators operate at no load at 50 Hz. the frequency at which they would operate with a total load of 600 MW is

A. 48.50 Hz
B. 47.69 Hz
C. 46.82 Hz
D. 49.04 Hz

Show Answer

Answer: B

Share your understanding of this question with the correct explanation.

B. 47.69